Under which condition is a transformer's rating additive?

Enhance your skills with the Transformers Test 1. Utilize flashcards and multiple choice questions, each accompanied by hints and explanations. Ensure you're fully prepared for your exam!

Multiple Choice

Under which condition is a transformer's rating additive?

Explanation:
When multiple transformers are connected in parallel, their kVA ratings can be added only if they will share the load evenly. This is typically true for small distribution transformers up to 200 kVA that have a primary voltage of 8,660 V or less. At these lower voltages and modest sizes, the impedances are such that each unit carries a proportional portion of the load, so the total rating is the sum of the individual ratings. If the voltage is higher than 8,660 V or the transformers are larger than 200 kVA, unequal impedance can cause one unit to take more load than another, making simple addition unreliable. Isolation transformers, on the other hand, are not intended to be paralleled for increasing rating.

When multiple transformers are connected in parallel, their kVA ratings can be added only if they will share the load evenly. This is typically true for small distribution transformers up to 200 kVA that have a primary voltage of 8,660 V or less. At these lower voltages and modest sizes, the impedances are such that each unit carries a proportional portion of the load, so the total rating is the sum of the individual ratings.

If the voltage is higher than 8,660 V or the transformers are larger than 200 kVA, unequal impedance can cause one unit to take more load than another, making simple addition unreliable. Isolation transformers, on the other hand, are not intended to be paralleled for increasing rating.

Subscribe

Get the latest from Passetra

You can unsubscribe at any time. Read our privacy policy